Create and Assign HVAC and DHW systems

It is recommended that HVAC and DHW systems characteristics for <VE> Compliance analysis are specified within the framework of Apache Systems. Apache Systems provide a robust and uncomplicated system model that has been harmonised with that provided in iSBEM with the aim of providing a point of reference and common ground between these alternative compliance methods.

Systems are one of the aspects of building design where substantial carbon emissions improvements can be introduced. The system data is therefore under your control, and it is shared between the real building (as displayed in Apache View) and the actual building (as displayed in <VE> Compliance).

The Apache System HVAC model has three key parameters, which can be defined in summary as follows:
SCoP – the efficiency of the heating system
SSEER – the efficiency of the cooling system (if present)
Auxiliary Energy Value – energy required for fans, pumps and controls

These are the most important parameters featuring in the calculation of the energy consumed by the space heating and cooling systems. Taken together with the fuels specified for heating and cooling, they encapsulate most of the important data about system performance in relation to carbon emissions.

On the Apache System dialogue there are other parameters that are linked with the heating and cooling system efficiencies and do not represent independently editable settings. For example, the heating system’s Generator seasonal efficiency and Heating delivery efficiency are linked to the SCoP by the relation

SCoP = (Generator seasonal efficiency) × (Heating delivery efficiency)

so that in terms of carbon emissions they can be viewed as secondary to the SCoP.

On the cooling side an analogous relationship exists between SSEER and the following parameters:

EER – the cooling system generator energy efficiency ratio or COP
CDE – the cooling delivery efficiency, and
HRP – the heat rejection pump and fan power fraction

namely

SSEER = EER * CDE / (1 + (EER + 1)*HRP)

In terms of carbon emissions EER, CDE and HRP can thus be viewed as secondary to the SSEER.

These ‘secondary’ parameters are important for certain design tasks in Apache View – for example the calculation of boiler and chiller loads. But for <VE> Compliance, SCoP and SSEER are the key efficiency measures.

Auxiliary energy value is a concept that has been developed in connection with the NCM methodology. This parameter indicates the power consumption of fans, pumps and controls associated with the space heating and cooling systems. It is expressed in terms of Watts per square metre of floor area served, and is incurred when the heating and cooling systems are running.

Parameter values can be entered directly into the Apache System dialogue. But it will usually be appropriate to make use of the UK NCM System Data Wizard to assist this task.

The UK NCM System Data Wizard has been developed as a replica of the analogous facility in iSBEM. Its purpose is to guide you through the process of describing the system properties and to generate values for the three key parameters.

In addition to the key parameters mentioned so far, there are other system parameters of importance such as heating and cooling system fuels and ventilation heat recovery effectiveness. These are also generated automatically from data entered in the wizard.

More information on using the wizard is provided in the <VE> Compliance User Guide.

New nomenclature for heating, cooling efficiencies has recently been introduced that aligns <VE Compliance> with the NCM. Definitions of these can be found in the DCLG document ‘Non-Domestic Heating, Cooling and Ventilation Compliance Guide’. This is freely downloadable from the DCLG website:

http://www.odpm.gov.uk/index.asp?id=1130726

SCoP and SEER values for commonly available plant can be found at:

www.eurovent-certification.com

The Apache System approach to DHW systems is slightly different from that adopted in iSBEM, but allows essentially the same flexibility. By default DHW is assumed to be the supplied by the same Apache System as the space heating system. If the building has a separate DHW system this can be created as an Apache System and connected to the rooms it supplies by means of the DHW System selector on the Room Data System tab. The efficiency of the DHW system must be expressed in terms of a generator (eg boiler) efficiency and a DHW delivery efficiency, the overall efficiency of the system being the product of these two efficiencies.

Note that Apache Systems may be imported from other projects on the back of Room Templates, allowing system data to be transferred between projects.

While the real (Apache View) and actual (<VE> Compliance) systems are in most respects identical, one difference is enforced in <VE> Compliance because of the way minimum ventilation is specified in NCM. For the real building there are controls on the Room Data System tab allowing you to specify air supplied to the room in the form of a ‘System air supply’. In <VE> Compliance all such air supplies are handled by Auxiliary Ventilation air exchanges, and for this reason the System air supply is disabled in this View. Following on from this the settings in Apache Systems dealing with setting the condition of the System air supply do not play a part in <VE> Compliance. In <VE> Compliance, ventilation is always supplied to rooms (or their terminal HVAC units) at outside air temperature.